Hi Everyone.
 
I have a suburban NT-16 furnace in my 1988 Toyota Odyssey. Back in 2019 I was having issues where the fan would start, but the ignition sequence never happens. To resolve it back then I bought a replacement board from ebay like this one: https://www.ebay.com/itm/386313082243?mkcid=16&mkevt=1&mkrid=711-127632-2357-0&ssspo=n-ju0w2ptyy&sssrc=2047675&ssuid=1-1GOiu-Twm&widget_ver=artemis&media=COPY. It solved the issue for me at the time, but the issue has returned.
 
I've done some troubleshooting steps including:
-Test the propane supply by replacing the regulator
-Bypass the propane plumbing by connecting the tank/regulator directly to the inlet on the heater
-Test sail switch with continuity tester (good)
-Test resistance over both propane valves (40-45 ohm, good)
-Check for voltage to the control board (good)
-Check for voltage at the propane valves 30+ seconds after fan start (no voltage)
 
I think this isolates the problem to the board.
 
Does anyone have experience with these? Are the newer boards unreliable? Should I buy another one or potentially a Dinosaur control board (https://www.dinosaurelectronics.com/UIB_S.htm)? Should I bail on the whole thing and replace the whole furnace (either with another NT-16 or maybe something else???)?
 
Thanks for being a great group.
 
 
Edited by GinjaTurtle
Posted

Dinosaur boards are good quality. One nice feature is they will attempt to light the furnace 3 times before shutting down. Rather then once like the factory board.


 

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...